Fire Alarm Integration with Aero X1100 Master controller & V100 Interfaces
When a Fire alarm input configured on a V100 AC Fail input was triggered, the Door Unlock command is successfully sent to all interfaces & it was verified from the door status page. Only magnetic locks connected to Strike Relay # 2 Unlocked but, magnetic locks on Strike Relay # 1 did not unlock i.e., The relay did not energize.
If we send a door unlock command from the door status page to Unlock the first door on the V100 it works normally without any problems & door access is also working normally. This issue occurs only during a fire alarm trigger.
|
The firmware of the Aero X1100 was upgraded from version 1.30.4 (671) to Version 1.31.0 (678).
After FW Upgrade the Fire alarm trigger unlocked all the doors properly.
|